Deye 8KW inverter not showing the KW consumption and Grid feed values
Need some advice.
I have the Deye 8KW for about 6 months and added the Neutral bonding rele as per the manual to ensure ELU remains functional when Utility falls away. I used the ATS port to power the rele and activated the Signal Island Mode to activate the rele when Utility falls away. Nothing else was changed!
Since then, the Inverter does not read/register the consumption "KW" or Grid feed "KW" or PV "KW" as it did prior. (PV "kw" only shows when it is charging the battery until the battery is 100% when Utility is present).
When Utility falls away and the inverter is running from backup all the "KW" readings return to the screen as normal until Utility returns again.
Any ideas to share on the reason for this, I suspect it might have something to do with the software version installed that might require a update?
Current:
Protocol V0.2.0.1
HMI VC3.4.9
MAIN_1 V3.8.8.0
MAIN_2 V0.0.0.0
With Utility on.pdf Utility Off.pdf