Posted December 20, 20222 yr My mains supply is over 5 meters away from my inverter so the leads from the supplied CT clamp dont fit. I paid for a solar supplier to see what can be done and they suggested installing the GivEnergy LoRa Wireless RS485 transmitter and receiver to wirelessly supply the inverter with the CT clamp readings. They have connected the lead to the CAN input and set as Wired CT. There is no load showing on the inverter. How do I get the load to show?
December 20, 20222 yr 3 minutes ago, DeborahJ said: My mains supply is over 5 meters away from my inverter so the leads from the supplied CT clamp dont fit. I paid for a solar supplier to see what can be done and they suggested installing the GivEnergy LoRa Wireless RS485 transmitter and receiver to wirelessly supply the inverter with the CT clamp readings. They have connected the lead to the CAN input and set as Wired CT. There is no load showing on the inverter. How do I get the load to show? Seems odd to have you buy something extra when they could have just extended the CT cable using ethernet cabling. It sounds like the CT was installed incorrectly; either its facing the grid (and not the inverter) OR it was installed onto the wrong pins. Either way they need to come fix it for you
December 20, 20222 yr Author The arrow is facing the fuse board when I take the clamp off. Should it be the other way around? They have been out twice now and still perplexed. They are a proper solar installer!
December 20, 20222 yr Is it between the Inverter and the DB board OR between the Main incoming line and the DB board?