Sunsynk DC on/off switch


Vissi3

Recommended Posts

Going to assume you have a sunsynk as i have no other info to go on apart from your image. Yes you can switch PV off on the PV switch on the inverter. You can then drop / switch off the PV breakers in your PV box - this should then render the panels inert. Remember to disconnect the MC4 before starting the work on the panels. The Inverter + batteries will still continue to power the house should eskom drop

@Steve87 - anything else I've left out?

Link to comment
Share on other sites

just for clarification -

Edit:
Shutdown process:

1. Flip the Change Over Switch to Grid (To power the house from the Grid and bypass the system) - only if you want house running off ESKOM only - ignore if you still want the inverter to be on
2. Flip the Inverter breakers Off in the DB Combiner Box (same as above)
3. Flip the PV (DC) Isolator on each Inverter Off then switch off DC at inverter

PV is now safe to work on.

Startup process:

1. Flip the DC switch on inverter to on then PV (DC) Isolator on each Inverter On 
(WAIT for the system to startup and Normalize, at this point you will see the DC(if during the day and you have panels) and AC lights. The NORMAL light can take 60-120sec to illuminate you will hear the relays when this happens.)
 

Edited by mzezman
Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...