I am still quite new, I just want to check is this is normal. My SNA5000 has no problem carrying all my normal household loads during loadshedding. But it has been cloudy all day and this morning my inverter tripped when I started my vacuum cleaner and now again when I started my chainsaw. I checked several times, it starts ok when the sun peeks out, byt purely off the battery, nope. I have a Dyness 4.8 battery with the discharge limit set to 40A in the inverter. I know things with electric motors draw a lot during startup, but I did not think it would trip the inverter. 

Link to comment
Share on other sites

25 minutes ago, eugenedp said:

I am still quite new, I just want to check is this is normal. My SNA5000 has no problem carrying all my normal household loads during loadshedding. But it has been cloudy all day and this morning my inverter tripped when I started my vacuum cleaner and now again when I started my chainsaw. I checked several times, it starts ok when the sun peeks out, byt purely off the battery, nope. I have a Dyness 4.8 battery with the discharge limit set to 40A in the inverter. I know things with electric motors draw a lot during startup, but I did not think it would trip the inverter. 

One can be 90% sure your vacuum cleaner as well as chain saw has a surge power that exceeds the 1920W that the 40A setting from the battery allows.

Link to comment
Share on other sites

Thank you. I think you may be correct. I have now changed it to 50A - the battery's max. But I still have the same problem. But that is only 2400W, Still too little I think. I will have to live with it for now, No money for another battery. Although I see the prices have come down a lot recently.

 

Link to comment
Share on other sites

48 minutes ago, eugenedp said:

Thank you. I think you may be correct. I have now changed it to 50A - the battery's max. But I still have the same problem. But that is only 2400W, Still too little I think. I will have to live with it for now, No money for another battery. Although I see the prices have come down a lot recently.

 

Yes that is the problem with a 0.5C battery. It is allowed to use 100A for 15sec. So may be you can change the setting only for when you want to try and use the saw. I would however limit the use of the saw to periods when you have grid. Not worth it to risk overloading the battery.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...