Dyness DL5.0C and Victron compatibility problem

Featured Replies

Hello to all!

Just installed a new off-grid system with Victron Multiplus II 48/5000/70 and two Dyness DL5.0C. Both are completely new, just purchased (Victron with the newest FW). The Dyness DL5.0C was manufactured on 17.06.2023, FW V95.1.
I found in the documentation (attached, about Victron and Dyness integration) what some data under menu DETAILS (what is planned regarding the document to implement, the document looks quite old) must be displayed, but actually they are missing. There is no such menu at all in the new system. It means battery BMS is not sending them to Victron.
Details must include: cell voltage, max and min temp, number of modules, capacity like described in your documentation.

My questions are:
1. Did DYNESS implement sending DETAILS to Victron like described in attached documents?
2. Maybe DL5.0C has old FW and needs to update FW to newest one with all data transferring from BMS DL5.0C to Victron?
    I know the same story with another person (another installation) with battery DYNESS DL5.0C manufactured 06.2024 and newer FW (V96.1).
3. Maybe newest version of the installation manual for Victron and Dyness is exist?

Regarding Victron support's answer, it is Dyness's responsibility to send all data to Victron, and they are missing.

real data from new system.JPG

planned details2.JPG

DYNESS VERSION.JPG

common real.JPG

Dyness and Victron connection instruction-EN.pdf

Edited by Andy0

  • Author

The topic is closed, thank you. Solution - changing the DIP switch setting on the Master battery to 1100 (not described in the manual).

  • 1 month later...
On 25.10.2024 at 20:24, Andy0 said:

Тема закрыта, спасибо. Решение -  изменение настройки DIP-переключателя на Master-аккумуляторе на 1100 (в инструкции не описано).

Good day. Do you know if it is possible to access the same data on Dyness A48100, using DIP switches?

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.