August 17, 20206 yr Good morning. Quick question on Victron Multiplus II. Is the power on AC-2 completely un-invertered and “dirty”? Our area experiences bad power. I would like to run a ITS hear-pump on AC-2 out and, as the ITS is vulnerable to spikes, hoped that Mutiplus would reduce the impact?
August 17, 20206 yr 1 hour ago, Mike Charlie said: Good morning. Quick question on Victron Multiplus II. Is the power on AC-2 completely un-invertered and “dirty”? Our area experiences bad power. I would like to run a ITS hear-pump on AC-2 out and, as the ITS is vulnerable to spikes, hoped that Mutiplus would reduce the impact? When connected to the grid, both AC-1 and AC-2 are connected to the grid and are, as you put it, un-inverted. But the Multi will disconnect from the grid if the voltage moves out of the acceptable range, which should help. Personally, I'd put in some SPDs (surge protection devices). Just remember to put them on the grid side BEFORE the RCD (aka earth leakage).