June 14, 20215 yr Good day, I have a Kodak OG7.2 inverter with 2 strings of 9x 335W panels each, connected to a 4 x US3000 battery bank. I would like to find out the effect of having the same address on all 4 batteries. Previously i had given them different addresses, the first being master and others slave, but the batteries would go into alarm. I do not a Battery software to check, but on putting the similar address on all, it went off. thank you. Leonard
June 14, 20215 yr The 3 address switches are only set to values other that 0 on the Master in each group. If you have only 1 group (8 or fewer batteries) all the switches should be off. The system assigns slave addresses in sequence starting with the one connected to the master.