I've included my settings for the 3 Axpert cluster that I have installed along with some of the thinking behind each option (based on my understanding). The system has been pretty solid in this configuration using AICC to monitor and control.
Firmware 72 40 and 01 24 respectively
Pretty happy with the charging that I'm getting:
going to float just after 12:30 (BMV is triggered to 100% a bit earlier...)
01 SBU
This mode is for on-grid use where you want to minimise grid usage. It will use the battery whenever solar is not available. It will only use the grid when the battery gets low. Link
02 70
This is within the limits of my battery bank - i.e. I can safely charge at a total of 210 Amps for the 3 Axperts combined. Solar can provide roughly 60 Amps maximum per Axpert (3kW). This will set the upper limit for solar charging and should we within the limits of connected batteries.
03 UPS
Conservative setting for grid voltage range i.e. if grid falls below 170V or rises above 280V it will be deemed to be unavailable
04 SdS
Inverters should remain on regardless of load
05 USE
User defined battery settings
06 LrE
Personal preference - I have protection breakers installed on all circuits supplied, so comfortable to restart in the event of overload
07 trd
More worried about temperature - so disable restart for overheat
09 50
50hz for SA
11 10
Small charge current from grid if the batteries dropped below SOC specified in AICC
12 45
Lowish voltage for back to utility - this is a fail-safe in the event that AICC doesn't switch for some reason and the batteries are being drained. This is an anti-nuisance setting to avoid accidental switching in the event of high load walk-ins.
13 50
Lowish voltage for back to Solar - shouldn't need this since AICC is in control, but will avoid unnecessary use of grid if the Axperts switched.
16 CSO
In the event that the batteries drop below SOC specified on AICC, use grid to trickle them up to avoid standing discharged (limited by setting 11). Useful for a 'full charge day'
18 BOF
No beeping
19 KEP
Stay on the selected screen
20 LOn
Keep the back-light on
22 AOF
No beeping
23 bYE
Enable bypass in the event of overload
25 FEn
Not really getting any faults, but keep them when they happen.
26 56
Specific bulk charge voltage for my bank
27 54.8
Specific float charge voltage for my bank
28 PAL
Parallel mode
29 44.5
Last resort cut-off voltage in the event of no grid.
30 ONE
As long as one Axpert has PV available, honour setting in register 1
31 SbE
Solar balance enabled for maximum utilisation of solar energy.