geert got a reaction from esmail-kassir in How to acces my inverter with my Windows PC without serial cable ?goto www.dessmonitor.com , login with the same account as the one from your Android.
-
geert got a reaction from Cakrawerdi in Shoto 5.12Kwh BMS to computer cablehello guys,
Someone know the administrator password for PMODBUSTOOS (I guess it is the same as for the PBMSTOOLS) ?
This Pmodbustoos is the only software that works, I cannot make the Pbmstools to work, it times out on the "serial port" - same cable, same com-port
I use the USB to RS485 adapter.
-
geert got a reaction from zsde in Max VOC per PV input - Axpert MAX II 8kw or cloneHi ZSDE,
Thank you VERY much for your answer! I was thinking the same, but had some doubts...
I have 6 panels (550W - VOC 49VDC) in serie on each input (total of 12 panels - 6600W - 3300W per input)
That should be good, right? Because I already have 2 inverters that died on that installation, one Sorotec 8kw, one SAKO sunpolo 8kw
The Sorotec inverter works a little bit, meaning it just does strange things, knowing for sure that the panels should give min. 5kw output (full sun), at a load of 500w / 1kw / 2kw it takes power from the grid. Even sometimes there is a load of e.g. 300watts, it shows that it takes 2300 watts from the panels.....
The SAKO give: running status fault, no AC output, even without PV input.
I am sure about the whole installation, PV connection strings into the inverter (polarity), no voltage leak, etc... I measured everything with a voltmeter. (I have around 282 VDC
per string)
SO I was wondering about the Max VDC input per MPPT. The word "array" confuses me as in "Maximum PV array Open Circuit Voltage"
thank you