Hi Mike
We have installed the (20160412) firmware from Creovision 20160412 Firmware Im not sure if this is the latest but we are getting the Fault on this firmware version.
Has Voltronic sent you the latest firmware?
" You need to relax the earth leakage value in the system " Is this setting in Solarpower software?
Thanks a lot.
Hi Guys
Thanks. The inverter is grounded to the main db board ground/earth bus bar.
I will get the electrician to test the ground ohms at the inverter and report back.
Hi all
We have installed a Inifini 10kw as per CreoVision"s "infini 10kW Modbus Grid Limiting Installation Guide" Thanks to Peter for his hard work.
However we are experiencing a Caution / Fault in the event log (no electrical ground) [19]
As soon as the AC breaker on the inverter is switched on the Ground fault [19] appears and the inverter goes into a fault mode
Our electrician has tested the earth/grounding and is getting around 10-15 ohms.
Has any one experienced this issue and or can help in CT?
Thanks.