Afrikaner got a reaction from hvl2 in Kodak 7.2kW problemOky. Setting 1 must be in sbu mode. For those who wants a full battery when loadshedding start. Make setting 12. 51 and setting 13. 53 or 52 54. And here is the problem setting that solved everything after nearly replaced all my codac inverters. Setting 16 must be on ....SNU!!!!. Some of my 5kw inverters must have little tweaks for it to work as intended. But let me know if this fix you problems. Im also playing around with firmware now . Remember setting 12 and 13 bust be 2v apart
-
Afrikaner got a reaction from jumper in Kodak 7.2kW problemThe technician im working with is learning the settings with me since im the only instalation he made that wanted this kind of setup. The supplier from capetown did phone someone in eu today about one of my 5kw inverters that run in paralel mode that wont connect after repairs was made on him. F81 error. But anyway we ask them for allot of assistance on personal needs. These kodac inverters is excellent for offgrid use. The ones on my home works perfect.
To give advice for all people who is not ofgrid and is connected to utility in south africa. During loadshedding times there is allot of inverters breaking from all brands even the most expesive ones because when eskom puts the power back online there is spikes and dips in the line
What i did was to put a relay at my mains. When power comes online the relay wil count 2min down before it will let power go through
After that i have another relay that when there is a 5% spike or a 5% dip on voltage it wil also take utility ofline
Since i did this i had no more inverters just breaking down for no reason
I will gladly help someone ill keep an eye on this thread