Everything posted by DanieF

  1. Thank you Jacques. I will test it out tonight.
  2. I have a Kodak 3.6 Hybrid inverter. I have 2xPylontech 2000 batteries and 4x460w solar panels connected to it. I noticed that after sunset, the battery will charge to 90% (which is the SOC setting), and immediately discharge or consume the battery once it reaches 90%. This happens while the grid power is on. It does not seem to stop. Is this normal? I do not see a setting that might might explain this behavior. The one setting on the battery I can change is set to "battery reserve" mode
  3. i followed your advice jumper and that did solve the problem. The earth leakage was installed before the inverter. I moved it to the outlet and no more trips. Thank you for the advice.
  4. Thank you Beat. it does make a lot of sense but I do not have any fridges on the inverter's output. It does make me think that the problem might be with the florescent lights or the energy savers. the other loads are: my laptop, wifi(12V) and computer monitor. I will also have a look at what you recommended jumper. i do have an earth leakage going to the inverter and not on the output of the inverter.
  5. I have a Kodak 3.5kw inverter with one Pylontech US2000 battery. My emergency supply from the inverter is all the lights in the house and my office (Monitors + wifi router). Usually the load is between 200-400watt and it never exceeds 400w. I have a problem where I get a trip most of the time when there is load shedding or when i switch off the mains. The inverter gives me an "AC overcurrent" error. This error is not discussed in the manual. If you leave it for +-5min, the inverter comes on by itself and keeps running. No trips after that. it also does not happen all the time, but it does happen more than not. I can't figure out what the cause is. Are there any suggestions?

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.