Trying to get to grips with the RCD tripping issue and get a solution.
Background:
I recently installed a 5kW SunSynk Inverter with a Hubble AM2 5.5kW Lithium battery for a friend. All are working except that the RCD feeding the Inverter trips when the Inverter switches back to the Grid. I did some test and I recon I know what the issue is.
Below is my take on the problem and some options to work around it. I will appreciate any input as I can't test until July as I am out of Country. I am not an Electrician but electronics is my bread and butter.
-------------------------
Disclaimer: My understanding of the fault maybe wrong and the suggestions listed here is not tested at all. The diagrams are just for illustration purposes with just the basic elements. No Surge Protection devises, etc are shown.
--------------------------
Note: There should always be an Earth - Neutral bond on the Grid Feed. When the Inverter is in "Island Mode" it will not draw power from the Grid and therefore the Inverter Feed RCD can’t trip when the Inverter is running in Island Mode.
Figure: SunSynk Inverter ATS240V output controlling the Earth-Neutral-Bond-Relay switching as recommended by SunSynk.
1: GRID Power is UP: When the Grid is UP (live) the Earth-Neutral bridge will be at the Grid. The Inverter's ATS240V signal will be off and the Earth-Neutral-Bond-Relay de-energized. . All OK
2: GRID goes down: When the GRID power goes down, the Inverter will energized the Earth-Neutral-Bond-Relay. The Earth-Neutral bond will now be at the Output of the Inverter that will also supply power to the Essential Loads. . All OK
3: GRID restored: When the Grid comes back ON the Inverter will take 1-2 minutes before it will switch back to the GRID.
a: During this time the Inverter will still generate power for the Essential Loads with the Earth-Neutral Bond at the Output of the Inverter.
b: When the Inverter switch back to the GRID it will also disconnect the Earth-Neutral Bond at the Inverter Output (ATS 240V signal goes OFF). All should be OK provided the Earth- Neutral bridge and Power transfer happen at the same instance.
With my Installation the Inverter Feed RCD trip every time at this point. This is with SunSynk Firmware version; MCU:3374
I manually cut the Earth-Neutral bridge just before the Inverter reverted back to the Grid as a test. That will prevent the RCD from tripping. That proves to me that the ATS240V signal is a fraction too late (for my install and many others it seems). According to this video by Keith https://www.youtube.com/watch?v=QtDblj7MMjY (at 2m15sec) he mentioned a delay is programmed in. I am not sure if that delay is when the Grid goes down or come back on, or both.
In my opinion SunSynk should add another setting in the Software where one can adjust/optimize the ATS signal timing vs Changeover time.
It seems these are the main solutions that the installers go for
No RCD that feeds the Inverter
Use the Grid Feed to control the Earth Neutral Bridge Box supplied.
Notes on the above:
No RCD:
Simple solution and not a requirement because of downstream RCD's? BUT, the Sunsynk Operators Manual recommends a Type A, 30mA instantaneous, 2 pole RCD feeding the inverter. Keith from SunSynk also mentioned that an RCD should be fitted. As I am familiar with most of the electronic components that are involved within an Inverter I understand why SunSynk insist on one. Your choice, I would not go without an RCD. I could not find a Type A anywhere, nether mind a sales person that know that there are different types. However I don’t think that not using a Type A is the problem.
The Earth-Neutral Bridge Box:
When the Grid comes back ON the Earth-Neutral bridge is immediately broken while the Inverter still provides current to the Load until it switch back to the Grid. During that 1 - 2 minutes there will be no Neutral bridge (floating Neutral) until the Inverter switch back to the Grid!
Workarounds:
Figure: Workaround 1
Workaround 1: GRID Feed controlling the Earth-Neutral-Bond-Relay switching
The GRID voltage controls the Earth-Neutral-Bond-Relay. The moment the Grid goes down the N/C contacts closes bridging the Earth and Neutral at the LOAD output of the Inverter. . All fine.
But, when the Grid comes back ON this bond is immediately broken while the Inverter still generates the current until switchover time (1 - 2 minutes). That will result in a floating Neutral until the Inverter switch back to the Grid! (not OK)
Fig: Workaround 2a
Using a Changeover Contactor switched by the Inverter's ATS240V signal
When the Grid is UP there will be no output from the ATS240V, so the Earth-Neutral-Bond-Timing-Contactor will be de-energized. The Grid Power will then flow through the N/C contacts to the Essential Loads bypassing the Inverter. The Earth-Neutral Bond will be at the Grid Feed.
When the Grid goes down the ATS240V signal will energize the E-N-B-T-Contactor transferring the Essential Loads to the Inverter. The Earth-Neutral bridge is then at the LOAD output of the Inverter.
If the Grid comes back ON, for the 1st minute or 2 the Inverter will keep on providing power before the ATS240V signal will fall away. The E-N-B-T-Contactor will then change back to the Grid.
Workaround 2b
Similar to 2a, except if 2 Contactors is used.