Dear Godwell
I hope this finds you well.
I have 3 x Dyness 4800 batteries hooked up to a Sunsynk 8KVA inverter. We are having an issue where the batteries are tripping if the load on the batteries exceeds 3KW.
If I understand correctly, at a discharge rate of 0.5C, the batteries should be able to handle a max load of 4.8 x 3 x 0.5 = 7.2 KW. With the batteries tripping at 3KW, Im getting less than half the load.
See below the current battery settings on my inverter:
Please help!
Kind regards
Mohamed