Hello Everyone. Purchased about half year ago this unit POW-HVM PRO 6.2M-48V.
All connected respectively with line, neutral, ground in and out.
I am expiring some weird issue on both output modes SBU and SUB.
I have 3 phases after my electricity meter.
1. In SUB mode voltage on out and in seems fine 230 volts.
Let's say i have Loads 2 kWatt and PV load also 2 kWatt, from grid it's consume about 150-200 watts, which is ok. But constantly every 15-30 sec PV drops to about 1.2-1.5 kWatt and grid consume respectively 150-200 + different's 500-700 watts, and after it's works good, and cycling again. The same situation when i tried to export all load back to the grid. One of my friends have 4.2 unit without this issue.
2. In SBU mode here is my voltages between:
AC IN-OUT neutral-neutral - 120 volt
AC IN-OUT live-live - 115 volt
AC OUT neutral-ground - 117 volt
AC OUT live-ground - 117 volt
AC OUT live-neutral - 230 volt
AC IN neutral-ground - 0 volt
AC IN live-ground - 230 volt
AC IN live-neutral - 226 volt
AC OUT neutral-IN live - 344 volt
If ground disconnected from inverter the voltage between grounds 117 volt
Also, almost all light are flickering a bit in SBU mode(SUB not flickering)
If i check with phase detector in socket of my house it's shows like i have 2 Phases(but lights on both with lower light as usual), in SUB mode it's lights only one phase and much brighter.
I have 2 grounds outputs, one on box and another near AC IN (please see attachment).
Maybe it's related to wrong connections neutrals and ground?
I would very appreciated if some one can guide me in right direction to resolve those issues.