8kw Deye Inverter and Kodak Batteries
Thank you all, i will set them up accordingly
-
8kw Deye Inverter and Kodak Batteries
Thank you , I agree
-
-
-
8kw Deye Inverter and Kodak Batteries
Can Kodak Lithium Batteries be successfully run on a DEYE inverter?
-
Inverter specs
Thank you, I will definitely be very careful, none of the PVs are not currently earthed, something I stiill have to do... I will run new cable tomorrow, leaving them in sets of 3, if that works as it should I will start connecting 6 together
-
Inverter specs
Thank you, I will check it, I tried to double check and used the same cable that runs from PV to inverter on the 3 panels in series, no problem, however connecting 3 extra panels on the same wire immediately results in error F23 is given. The same error on bank of 6 other panels. I have no surge arrestor connected currently, when I check the cable on the inverter side with 2 strings x 6 panels connected in series the voltages on both strings run almost identical outputs
-
Inverter specs
That is correct, it has the same label on the side of the inverter.
-
Inverter specs
Thank you for the reply, I have tried connecting 6 panels in series in a single string, however it gives me an F23 fault every time, when I reduce it to 3 panels in series, the warning disappears, F23: THE AC leakage current is trancient over current. What could that be?
-
Inverter specs
Here is the inverter specs.
-
Inverter specs
Hi Guys. I need assistance please, I have just bought a DEYE 8kw inverter, 12 x JA 450 W panels, 4 x 100 ah lithium batteries, i also have a 6 string combiner box with 1 string out. I can convert this to dual if needed. I am planning to use 4 strings of 3 panels connected in series, with obviously a single string to the inverter, is this the right way to go? 2nd question I have is, will a single input from the combiner box connected into the inverter be acceptable and still within the inverter tolerances for a single MPPT? Please excuse my ignorance. Advice would be appreciated
-
Narada Settings
Hi All. I need assistance please. I have just installed 2 x 100ah Narada lithium batteries on a 5kw kings inverter (full circle Solar). How do I tell the inverter what battery type this is, currently it os set to AGM, and working fine. I do however believe I should set it differently. Setting it to Pylon sets off alarms. The other option I see is "user defined", but that means setting a lot of parameters in other menus, ehich I am.not sure off. Can someone please assist. JOHAN
-
Narada and Pylontech
Thank you for the feedback, I will. Keep them separate.
-
Narada and Pylontech
Hi all, I have an Axpert 5kw inverter with 2 x 2,4kw/h pylon tech batteries. I Received a Nerada 100AH as a gift. I would like to increase the storage capacity of my system. , Is there any way in which I can make the 2 brands of batteries work together on the same inverter?
-
Solar Charging
Yes, I started the generator, lfp was running low as there is no sun at the moment. My lfp get me through a night no problem, I am definitely installing 6 new panels within the next 2 weeks. I am Also adding an additional 3,5 kw Pylon at the same time Panels are on the roof... So. Probably a 30 degree slope if I had to guess.
-
Solar Charging
-
Solar Charging
No I did not, unfortunately my laptop doesn't have a DVD /CD drive