Greetings
I need some assistance. This is what I have ...
2 * Axpert/Mecer 5Kw Inverters connected in parallel (SOLIAX5P)
12 * Canadian solar panels (325W each) - Separated in two strings, so each inverter is connected to 6 panels
4 * 3.5Kw Pylontech batteries (us3000)
I understand that program 2 must be set according to the number of batteries (N) * 37A (recommended for us3000). In this case we will have 4 * 37 = 148A
I am assuming I need to split this load for charging between the two inverters for program 02, so one inverter can read 80A and the other 70A to give me 150A, or alternatively make both of them 70A each.
Should the config be as follows then:
Program 02: 70A for the one inverter and 80A for the other inverter
Program 05: USE
Program 11: Not sure what to put here for either inverter, should be the same as program 02
Program 12: 46V
Program 13 48V
Program 26: 53.2V
Program 29: 47.0V
PS. I have bought the raspberry pi from centurion solar already
Thanking you in advance