Look at the frequency shifting settings. They need to be set up correctly else the system will experience problems especially if you lose the grid during a power outage and the delta inverters are not throttled back if there is excess power. Not all grid tie inverters play nicely in a AC coupled system which is islanded. We have had quite a process to get the Solaredge inverters to work with the victron in a AC coupled situation, which involved direct support from Solaredge. I don't know the delta situation first hand, but I can tell you that the settings are important for it to work correctly. Load shedding is going to be back soon and the last thing you need is for the grid to fail at 12noon on a sunny day with battery bank fully charged and low or no loads. Something will start to smoke and it most likely will be the Quattro