Wilfred's post in Axpert mks parallel installation was marked as the answerHi,
Keeping in mind that everything else is perfect......
So in short...
What comes to mind is the current sharing wires between the inverters and the parallel cards and cables between the inverters. All inverters should be connected to the same battery bank.
Usually at setting 28 on the inverter you have a option between PAL, SIG, PH1, PH2, PH3. You need to set it up as PAL, this mean it will run in parallel to the other inverters connected. Make sure all of the inverters are set at PAL (parallel)
Usually setting 01, 12, 13, 26, 27 and 29 will change on all slaves as soon as you change it on the master inverter.
Master inverter should be the inverter that starts up first. Order don't matter.
Hope this was what you were looking for.