Everything posted by CalmYourself
-
Goodwe + Pylontech US3000 only charging to 80%?
I didn't make any adjustments. My system still does sit at 88% for a while before jumping up to fully charged, probably related to unbalance between the cells and the BMS compensating. My DIP switches are all set to Off
-
Goodwe + Pylontech US3000 only charging to 80%?
Officially up to 100% today. So it took 2 and a half weeks.
-
Goodwe + Pylontech US3000 only charging to 80%?
I have 2x US3000 selected. I think it might be a balance thing. Over the last week and a bit the max charge has been climbing slowly. Today it changed to 90%. I'll post back here if it ever reaches 99%
-
Goodwe + Pylontech US3000 only charging to 80%?
Ah, there must be something else wrong then. I have my on-grid DoD set to 60% and the off-grid DoD set to 89% and my batteries still only charge up to 80%.
-
Goodwe + Pylontech US3000 only charging to 80%?
Oh that's great, do you by any chance know what setting it is @Maxibelgium? In the PV Master app, I can't seem to change the charge voltage or current and can only change the DOD settings for on-gird or off-grid.
-
Goodwe + Pylontech US3000 only charging to 80%?
Hi guys I have a recently installed Goodwe ES (4.6kw) setup hooked up to 2x Pylontech US3000's. I'm not sure if I've configured anything incorrectly, but the batteries only ever charge up to 80% SOC. Is there something I've configured incorrectly? (As a side question: is there a way to see the potential the panels are generating instead of having them track the load too?)