Hi @demaniak
With 3× older BYD 2.5 modules 7.7 kWh at 0.5C, you’re limited to roughly 3.8 kW continuous charge/discharge.
The 12kW Deye is too big for this bank it pulls hard on grid failure and trips the BMS.
Recommended settings:
Set battery to Voltage mode (not SOC)
Max charge current: 70–75A
Max discharge current: 70–75A
Discharge stop: ~48–49V
Charge end: ~54–55V
This should stop the shutdowns.
Long term you’ll need more storage capacity for a 12kW inverter that can charge and discharge at 240A 12.3 KW