February 28, 20224 yr Good evening I need help with installer code on Lux power registration for my client, I put in the wrong customer code and could not see his unit on my account to make adjustments on it for parallel settings is it possible to change the customer code?
November 17, 20223 yr You may find this info helpful: Luxpower Support Email: [email protected] JHB Tech manager Jonathan: +27 74 098 0707 JHB Support Manager Owen: +27 84 975 5067 Cape Town Support Manager Andy: +27 82 555 5077
November 18, 20223 yr Good day I have a 5kw Lux Power inverter paired with a Dyeness A48100 4,8kWh Lithium - ion battery. Unfortunately the battery does not communicate with the inverter, So we have been using it under "Lead-Acid". for the last 3 weeks or so it appears that our battery parameter settings were set to default resulting in the battery completely dying and the house without power, When it should of switched over to the grid. Yesterday I went through the Inverter settings using the luxpower monitor app, And for some reason my battery parameters were all reset to default (i.e Cut Off Voltage 42V, EOD Discharge Grid on 42V) I was only able to set the EOD Discharge Grid On voltage using the app. When I tried to set the Discharge cut off voltage it would give me "Operation failed, Error code 3". Therefor I opted to set those two values directly on the inverter using the LCD Display. This morning the battery cut out at about 2AM with 20% SOC Remaining, Indicating that the battery discharge cut off setting is working as it should however the End of Discharge Grid on setting is still not working despite the two settings being set to the same value of 47V according to the battery manual. I have changed the EOD Grid on to 47.7V from 47V in hopes that it will take effect tonight. Something to keep in mind is that In our 5 months of ownership we have not updated the inverters firmware Please advise on solutions to solve this problem. Kind Regards Brian Zeelie Edited November 18, 20223 yr by Bryan1
November 18, 20223 yr 26 minutes ago, Bryan1 said: Good day I have a 5kw Lux Power inverter paired with a Dyeness A48100 4,8kWh Lithium - ion battery. Unfortunately the battery does not communicate with the inverter, So we have been using it under "Lead-Acid". for the last 3 weeks or so it appears that our battery parameter settings were set to default resulting in the battery completely dying and the house without power, When it should of switched over to the grid. Yesterday I went through the Inverter settings using the luxpower monitor app, And for some reason my battery parameters were all reset to default (i.e Cut Off Voltage 42V, EOD Discharge Grid on 42V) I was only able to set the EOD Discharge Grid On voltage using the app. When I tried to set the Discharge cut off voltage it would give me "Operation failed, Error code 3". Therefor I opted to set those two values directly on the inverter using the LCD Display. This morning the battery cut out at about 2AM with 20% SOC Remaining, Indicating that the battery discharge cut off setting is working as it should however the End of Discharge Grid on setting is still not working despite the two settings being set to the same value of 47V according to the battery manual. I have changed the EOD Grid on to 47.7V from 47V in hopes that it will take effect tonight. Something to keep in mind is that In our 5 months of ownership we have not updated the inverters firmware Please advise on solutions to solve this problem. Kind Regards Brian Zeelie hi Brian - just a privacy note to remove your cell number from the post - its a public forum and not everyone does the right things Edited November 18, 20223 yr by mzezman spelling
November 29, 20223 yr On 2022/11/15 at 5:52 PM, RobM said: default customer code is inf01 worked for me Thanks for this - managed to use it and it worked great
November 29, 20223 yr On 2022/11/18 at 9:04 AM, Bryan1 said: Good day I have a 5kw Lux Power inverter paired with a Dyeness A48100 4,8kWh Lithium - ion battery. Unfortunately the battery does not communicate with the inverter, So we have been using it under "Lead-Acid". for the last 3 weeks or so it appears that our battery parameter settings were set to default resulting in the battery completely dying and the house without power, When it should of switched over to the grid. Yesterday I went through the Inverter settings using the luxpower monitor app, And for some reason my battery parameters were all reset to default (i.e Cut Off Voltage 42V, EOD Discharge Grid on 42V) I was only able to set the EOD Discharge Grid On voltage using the app. When I tried to set the Discharge cut off voltage it would give me "Operation failed, Error code 3". Therefor I opted to set those two values directly on the inverter using the LCD Display. This morning the battery cut out at about 2AM with 20% SOC Remaining, Indicating that the battery discharge cut off setting is working as it should however the End of Discharge Grid on setting is still not working despite the two settings being set to the same value of 47V according to the battery manual. I have changed the EOD Grid on to 47.7V from 47V in hopes that it will take effect tonight. Something to keep in mind is that In our 5 months of ownership we have not updated the inverters firmware Please advise on solutions to solve this problem. Kind Regards Brian Zeelie Hi Bryan did you manage to get this sorted? Dyness and Luxpower do definitely work together - just need to correct cable pinout and setting on the inverter itself
November 29, 20223 yr Hi Mzezman Yes it was actually a blown AC breaker and after replacing it the system is working well again thanks.
November 29, 20223 yr 36 minutes ago, Bryan1 said: Hi Mzezman Yes it was actually a blown AC breaker and after replacing it the system is working well again thanks. Ah nice - good to hear. Many happy generation hours ahead
February 21, 20251 yr On 2022/11/18 at 9:30 AM, mzezman said: hi Brian - just a privacy note to remove your cell number from the post - its a public forum and not everyone does the right things Hi Brian, did you solve your issue? As we have the same issue.