May 28, 20224 yr Morning all I split my distribution board into sections, running a 5kw system on each half My query relates to the ct installation 1. Must it be installed on the main incomer from the council that feeds both halves, or 2. Should it be installed on the individual feeders to the inverters
May 28, 20224 yr 6 hours ago, Bester71 said: Morning all I split my distribution board into sections, running a 5kw system on each half My query relates to the ct installation 1. Must it be installed on the main incomer from the council that feeds both halves, or 2. Should it be installed on the individual feeders to the inverters 1. The single CT is fitted on the main incomer between grid point and main switch. Arrow pointing towards inverter AFAIR. The arrow on Solis points to the grid side. 2. Only 1 CT is fitted on the incomer for the master inverter when used in parallel. If you split the DB for each inverter how do you work out the essential vs non essential loads?
May 29, 20224 yr Author Actually quite easy Section one = inverter 1 Section two = inverter 2 Section three = non essentials like underfloor heater etc all fed from common supply, which have an integrated generator on grid side for extended outages 14 hours +