June 30, 20224 yr Hi I'm considering getting an inverter generator to attach to my Sunsynk 5k inverter. This will mainly be for when load shedding has kicked up high and the batteries have not had a decent chance to charge, cloudy or night etc. The generator I've been considering is the Ryobi RG-2600i, so only 2200W output, which is more than enough to run the essential load, roughly 1kW when utility power off, and charge the batteries... I see in the Battery Setup -> Batt Charge screen you can set the max charge current for the generator, as with the grid charge. 1. would the Sunsynk use the generator power as it would utility power? i.e. use PV for load and utility/gen to top-up load and/or charge batteries? 2. is the gen charge value also used to set the max current drawn from the generator, load and/or charge, thereby not trying to pull more than the generator can supply? 3. can the generator be run when utility power is on? no real guarantee when utility is restored or just wanting to run the gen for regular use...
June 30, 20224 yr Author I may have found an answer to my question 3. I found a post on the Sunsynk form that states the inverter will use either the grid feed, with grid as the priority, or the generator but not both together. I can live with that, would then just run the generator occasionally, without connecting it to the inverter, to ensure it still runs...