August 4, 20224 yr Hi all I just recently had a system installed with a Dyness BX51100 battery I am running SolarAsssitant to monitor things. The battery info is giving really weird results - could the BMS of the battery be faulty? See the reading on pack 1.
August 4, 20224 yr You have two of these batteries? Are the dip switches set correctly? The 400A by itself with zero voltage and zero Watts is an indication of some sort of comms issue. Yes, it could be the BMS, but it could also be the comms connection to the inverter or dip switches not set correctly. Have you tried disconnecting the comms cable from the battery, then manually set your inverter in USE mode or non Li mode and set all voltages according to battery specs. Reboot the system and batteries and see if the battery readings in SA change afterwards.
August 4, 20224 yr Author Hi all I had to upgrade to a beta release of the SolarAssist software. All seems fine now excep that it reads the battery as 50Ah. But capacity SOC and Voltage readings look normal now at least.
August 4, 20224 yr 2 minutes ago, Douw Gerber said: Hi all I had to upgrade to a beta release of the SolarAssist software. All seems fine now excep that it reads the battery as 50Ah. But capacity SOC and Voltage readings look normal now at least. Hownare the batteries connected to the inverter and Solar Assistant? Only asking because I have some challenges getting the SA connection going on my end
August 5, 20224 yr Author 20 hours ago, mzezman said: Hownare the batteries connected to the inverter and Solar Assistant? Only asking because I have some challenges getting the SA connection going on my end Via a cable I ordered from SolarAssistant - Rasberry PI USB to Battery RS485 port Edited August 5, 20224 yr by Douw Gerber
August 5, 20224 yr Author 20 hours ago, Douw Gerber said: Hi all I had to upgrade to a beta release of the SolarAssist software. All seems fine now excep that it reads the battery as 50Ah. But capacity SOC and Voltage readings look normal now at least. SA got back to me to confirm that the Dyness reports 50AH but they are working on a fix for this. Its doesn't affect the battery runtime.
August 5, 20224 yr 2 hours ago, Douw Gerber said: Via a cable I ordered from SolarAssistant - Rasberry PI USB to Battery RS485 port Arent you using the battery RS port for the inverter bms?
August 6, 20224 yr Author 20 hours ago, mzezman said: Arent you using the battery RS port for the inverter bms? nope.
August 7, 20224 yr Aaah ok, then thats the issue i have. Will disconnect that one and use the SA one and see how thay goes. How does the inverter then know how to manage the battery though with the bms 'disconnected' for lack of a better word
August 9, 20224 yr Author On 2022/08/07 at 11:25 AM, mzezman said: Aaah ok, then thats the issue i have. Will disconnect that one and use the SA one and see how thay goes. How does the inverter then know how to manage the battery though with the bms 'disconnected' for lack of a better word The battery is pretty much managed by SA using the automatic power management features.