Hybrid inverter spec versus Battery Capacity (LiFePo4)

Featured Replies

Hi All, after much research I have sadly come to the realization that for the following system:

  • 5kw 48V Inverter
  • 5kw 48V 100aH Batter 

Due to the nature of the recommended charge and discharge for LiFePo4 batteries being 0.5C, I would only be able to discharge these batteries at 2.5kw (50aH) per hour, depleting them in 2 hours.

Thus my 5kw inverter is being wasted as it can only ever provide 2.5kW of power if I plan to maintain the health of my battery.

So if I want to run a 5kw inverter at full load, I would need 2x the battery capacity, effectively 10kwh of batteries.

Am I missing something, or is this a well-known limitation of these systems? Either I'd need 2x 48V 100aH in parallel or a 2x24V 100aH battery in series, but both would result in a total battery capacity of 10kwh, which is double the inverter rating. 

For interest, these are the spec sheets of the invert and battery I am considering

33 minutes ago, D3monhun73r said:

Hi All, after much research I have sadly come to the realization that for the following system:

  • 5kw 48V Inverter
  • 5kw 48V 100aH Batter 

Due to the nature of the recommended charge and discharge for LiFePo4 batteries being 0.5C, I would only be able to discharge these batteries at 2.5kw (50aH) per hour, depleting them in 2 hours.

Thus my 5kw inverter is being wasted as it can only ever provide 2.5kW of power if I plan to maintain the health of my battery.

So if I want to run a 5kw inverter at full load, I would need 2x the battery capacity, effectively 10kwh of batteries.

Am I missing something, or is this a well-known limitation of these systems? Either I'd need 2x 48V 100aH in parallel or a 2x24V 100aH battery in series, but both would result in a total battery capacity of 10kwh, which is double the inverter rating. 

For interest, these are the spec sheets of the invert and battery I am considering

No your 2x24V 100Ah will stil just give you 4.8kWh not 10kwh.

There are 3C batteries. Most are 1C. You have a choice if you buy a make that is only 0.5C 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.