Hello,
I have Infini inverter 3kw plus, now the neutral output have 120V is it Normal
can anybody share wiring the output, the neutral must be grounding or not
please share to me
Alkafak
Hi alkafak,
I suppose your inverter is working in offgrid mode. Then neutral from grid is different from neutral output inverter, because relay transfer is open, but you cant grond neutral inverter because if infini change to bypass, you would have a leackage fault. In some Axperts, when inverter change from bypass to Offgrid, a relay conects neutral to ground. I dont know how your inverter works, but there should be something similar.
3 minutes ago, Javi Martínez said:
Inverter ground, ACIN Gound, and ACOUT Ground, are joined in Grounding?
not, AC in separate and join the grid inverter and AC out is joined
In manual, it only appears:
"Be sure to connect L terminal of load to L terminal of “AC Output Connector” and N terminal of load to N terminal of “AC Output Connector”. The G terminal of “AC Output Connector” is connected to grounding of the load. Do NOT mis-connect."
4 minutes ago, Javi Martínez said:
I remember to have read three wires sould be joined. Can you try it?
Thank you Javi, i will try  to bounding all the ground, and see what happen
7 minutes ago, Javi Martínez said:
I suppose differential switch doesn´t work when you measure 120 v from neutral to ground, does it?
i used 10 A RCBO but not trip,