Aspire error code driving me nuts


Deonbayly

Recommended Posts

Hi guys

I'm totally off grid so any problems with water or power escalate extremely quickly! I'm tearing my hair out over this one.

I'm running my single phase borehole motor off solar and an Aspire 2,2kw LS inverter through a control box. This has been working great for a couple of years.

Yesterday I got Error A03 - Dry running  1. Water level in the well is low.
                                                                   2. Nominal power of motor is not setting.

We can rule out 1.

I changed the motor nominal power to 1.5kw, although in the past it was set to 2.2kw. This was just in case I forgot which pump is actually down the hole! I know, I know. Error persists.

Since (to my amateur logic) this looks like a low current error (it sees the pump as being out of the water = low resistance = lower amps?) I've been slowly reducing the nominal current setting, all the way down to 5A, but the error persists. The system is up for maybe 4 seconds before shutting down.

I've now got enough water left for maybe 2 days and I'm not sure what to try next!

Has anyone been in this situation or have any advice on what to try? 

Many many thanks!!

Link to comment
Share on other sites

1 hour ago, Deonbayly said:

Hi guys

I'm totally off grid so any problems with water or power escalate extremely quickly! I'm tearing my hair out over this one.

I'm running my single phase borehole motor off solar and an Aspire 2,2kw LS inverter through a control box. This has been working great for a couple of years.

Yesterday I got Error A03 - Dry running  1. Water level in the well is low.
                                                                   2. Nominal power of motor is not setting.

We can rule out 1.

I changed the motor nominal power to 1.5kw, although in the past it was set to 2.2kw. This was just in case I forgot which pump is actually down the hole! I know, I know. Error persists.

Since (to my amateur logic) this looks like a low current error (it sees the pump as being out of the water = low resistance = lower amps?) I've been slowly reducing the nominal current setting, all the way down to 5A, but the error persists. The system is up for maybe 4 seconds before shutting down.

I've now got enough water left for maybe 2 days and I'm not sure what to try next!

Has anyone been in this situation or have any advice on what to try? 

Many many thanks!!

What is the PV Array size you have connected and how are the labels connected? 

You mention you running of solar. Do you have no grid connected? 

Link to comment
Share on other sites

Manual says:

PV Module Selection:

When selecting proper PV modules, please be sure to consider below parameters:

1. Open circuit Voltage (Voc) of PV modules not exceeds max. DC voltage (450VDC).

2. Accumulated voltage of connected PV panels should be close to 330V for inverter with 220V output voltage.

To calculate PV module numbers in series (N) and in parallel (M), please follow below formula:

 For three-phase output:

 Imp>Po/(Kvo x 0.9 x M)

 For single-phase output, please use 2 times of PV power rating.

 Imp>2 x Po/(Kvo x 0.9 x M)

Po represents the rated output power.

Kvo is equal to 330V/345V/360V for 220V/230V/240V output voltage respectively.

 Maximum PV module numbers in series (N) > 330 / Vmp

We strongly recommend the total PV Vmp is around 330Vdc to get the optimum MPPT output.

Link to comment
Share on other sites

5 minutes ago, Deonbayly said:

Manual says:

PV Module Selection:

When selecting proper PV modules, please be sure to consider below parameters:

1. Open circuit Voltage (Voc) of PV modules not exceeds max. DC voltage (450VDC).

2. Accumulated voltage of connected PV panels should be close to 330V for inverter with 220V output voltage.

To calculate PV module numbers in series (N) and in parallel (M), please follow below formula:

 For three-phase output:

 Imp>Po/(Kvo x 0.9 x M)

 For single-phase output, please use 2 times of PV power rating.

 Imp>2 x Po/(Kvo x 0.9 x M)

Po represents the rated output power.

Kvo is equal to 330V/345V/360V for 220V/230V/240V output voltage respectively.

 Maximum PV module numbers in series (N) > 330 / Vmp

We strongly recommend the total PV Vmp is around 330Vdc to get the optimum MPPT output.

I see the manual and as you indicated the PV to be 2 times the motor size. Thus one should try to get to 330V and also 4.4kW of panels by having say series and 2 strings in parallel. Not a easy configuration. 

Previous question. Do you have grid connected? 

Link to comment
Share on other sites

Hi

Apologies, no, I have no grid connection.

I have used a generator before when I had to pump water in the dark. I tried that yesterday with the same result.

I may have some more of the same panels in the shed, I'll go and have a look.

Cheers

Link to comment
Share on other sites

19 minutes ago, Deonbayly said:

Hi

Apologies, no, I have no grid connection.

I have used a generator before when I had to pump water in the dark. I tried that yesterday with the same result.

I may have some more of the same panels in the shed, I'll go and have a look.

Cheers

If the inverter fails even with genny there must for sure be a problem. 

Or did you connect the pump directly on the genny and not via inverter? 

 

Link to comment
Share on other sites

I called the supplier. He suggests that I cut out the control box and wire the pump directly to the inverter as the inverter has its own controller.

I'm going to go and try that now....

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...