April 8, 20251 yr Does anyone have any idea what could be the problem if an RCT 1000VA UPS works in AC MODE only and does not work on battery mode even if I replace the two 12V 7.1AH batteries .I would be very grateful if someone has a service manual for the particular UPS .
June 3, 20251 yr Your batteries are not large enough... 2 x 12V x 7.4A = 170Wh, IF you could completely drain the batteries (not advisable...). With losses in the system, and only using 50% of battery capacity, you would need at least 2 x 50Ah batteries to be able to use the UPS for one hour.
June 4, 20251 yr On 2025/04/08 at 6:28 PM, josiah sakala said:RCT 1000VA UPSThis ups is sold brand new with On 2025/04/08 at 6:28 PM, josiah sakala said:12V 7.1AH batteriesHow the china factory rated this at 1000VA is unknown! I have opened a couple of blown 1000VA Mecer / RCT / K-Star / PSS line interactive units, they all come with this crappy battery setup. Why your ups is behaving the way it does - probably something on the pc bord.