Need help with Combiner box

Featured Replies

Good day,

When I bough the house there was solar installed. I have upgraded the inverter to Sunsynk 8kw, there was 12 x 265watt panels connected in 2 strings, then connected to 1 MPPT. Yesterday I replaced the 12 panels with 12 x JA Solar panels 615, 2 strings. But my Combiner box can take 5 strings but I see only 1 out for the MPPT.

Is there a way with the current combinder box to the Output be 2 x for MPPT’s?

IMG_0581.jpeg

8 hours ago, Morne van der Merwe said:

Good day,

When I bough the house there was solar installed. I have upgraded the inverter to Sunsynk 8kw, there was 12 x 265watt panels connected in 2 strings, then connected to 1 MPPT. Yesterday I replaced the 12 panels with 12 x JA Solar panels 615, 2 strings. But my Combiner box can take 5 strings but I see only 1 out for the MPPT.

Is there a way with the current combinder box to the Output be 2 x for MPPT’s?

IMG_0581.jpeg

Yes you can just do a few wiring changes and have 2 sets of surge arresters and with it the isolator for each string with the CORRECT fuses for you new panels.

9 hours ago, Morne van der Merwe said:

Is there a way with the current combinder box to the Output be 2 x for MPPT’s?

I would wire the negative of the one string to the left hand of the DC breaker and wire the negative of other string to the right hand side. From there go to the inverter. Bypass the whole box on the positive side.

2 hours ago, Morne van der Merwe said:

Good day,

When I bough the house there was solar installed. I have upgraded the inverter to Sunsynk 8kw, there was 12 x 265watt panels connected in 2 strings, then connected to 1 MPPT. Yesterday I replaced the 12 panels with 12 x JA Solar panels 615, 2 strings. But my Combiner box can take 5 strings but I see only 1 out for the MPPT.

Is there a way with the current combinder box to the Output be 2 x for MPPT’s?

IMG_0581.jpeg

Yes, but you will need some extra components.

Namely, an additional lightning protector, and an additional isolator.

You would also need to make more space in the box to accommodate this. As you would be running 2 strings only, you can remove 3 of the bottom fuses and 3 of the top fuses. You would also need to remove what I can only assume is the copper busbar from the top of the fuses, that combine it to 1 single line.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.