Hi Guys, Some advice here please,
I have a RCT ( Axpert ) 8KW - Max 11
Main Cpu firmware is 00054.01
Secondary firmware is 00022.11
Set for solar charging only
When set to SUB ( CURRENT SETTING ) The inverter works fine and draws from utility if pv is not enough. I'm happy with this.
As soon as the Batteries ( Pylontech with Bms ) hit 100% charge the inverter drops the PV and draws only from Utility.
When set to SBU The inverter does Not draw from PV at all. It still draws from Utility - not batteries- Although there is more than enough PV.
When the battreries reach 100% charge the inverter drops utility for a few seconds - Draws from the battery for a minute then Changes to draw from utility Only.
I have resorted to Dropping the AC breaker at sunrise then switching AC back ON at night.
ANY IDEAS ??
I'm in the process of adding the the battery bank this weel - Then hoping to use SBU as battery capacity will be more than enough to last the night.
I have tried another inverter ( Mecer 8kw ) Exact same issue.
ANY IDEAS ??
What is your cut off settings? And the SOC setting for returning to PV and battery when the set battery SOC is hit? My inverter worked similar to what you describe and those 2 settings where my culprit.
Hi Denns, I was under the impression that when I select Pylon in he settings - All the parameters are set automatically ?? Am I missing something? I did go through the settings and nothing can be changed manually