TERRENCE P got a reaction from james naidoo in SOLAR PANEL CONFIGURATIONUnfortunately he can't understand you and neither can I. Adjust VOC Upwards to Minus 5 Deg ???. Sorry for being Dumb.
He did see the inverter sticker etc . Now the installation is on hold ..... will cost me another call out but I can live with that to do the right thing here
-
TERRENCE P got a reaction from james naidoo in SOLAR PANEL CONFIGURATIONThank you so much for the response. Now I have a situation on my hands.
With the components mentioned what would you advise. Unfortunately the inverter and batteries have already been installed and working.
-
TERRENCE P got a reaction from james naidoo in SOLAR PANEL CONFIGURATIONHi Guys,
Some advice from you Solar Gurus Please. Easy one.
INVERTER
5KW OC ( AXPERT KING FAMILY )
Solar Charge - 80 Amps
Min Input solar - 40 Vdc
Max input solar - 145 Vdc
PANELS CS-585w-N X 6
Operating voltage - 43.3 vdc
open circuit voltage - 52.4 vdc
operating current - 13.52 Amps
Short Circuit current - 14 Amps
SO HERE IS THE QUESTION
My installer wants to use 2 strings of 3 in series then parallel into a 1 in 1 out combiner box .
With OSV the input voltage is 157.2 vdc And 27 Amps. ( Operating voltage will be 129.9 vdc ) He says this is perfectly fine and the higher ocv is nothing.
We initially asked him for 3 strings of 2 in series into a 3 string combiner box.
With this OSV is 104.8 and 40 Amps. We assumed that this was safest for these problematic Axpert inverters. But the installer says that this is a waste and too expensive.
Some advise will be much appreciated here as I want to address it before the connections begin.
-
TERRENCE P got a reaction from Virwat in SOLAR PANEL CONFIGURATIONHi Guys,
Some advice from you Solar Gurus Please. Easy one.
INVERTER
5KW OC ( AXPERT KING FAMILY )
Solar Charge - 80 Amps
Min Input solar - 40 Vdc
Max input solar - 145 Vdc
PANELS CS-585w-N X 6
Operating voltage - 43.3 vdc
open circuit voltage - 52.4 vdc
operating current - 13.52 Amps
Short Circuit current - 14 Amps
SO HERE IS THE QUESTION
My installer wants to use 2 strings of 3 in series then parallel into a 1 in 1 out combiner box .
With OSV the input voltage is 157.2 vdc And 27 Amps. ( Operating voltage will be 129.9 vdc ) He says this is perfectly fine and the higher ocv is nothing.
We initially asked him for 3 strings of 2 in series into a 3 string combiner box.
With this OSV is 104.8 and 40 Amps. We assumed that this was safest for these problematic Axpert inverters. But the installer says that this is a waste and too expensive.
Some advise will be much appreciated here as I want to address it before the connections begin.
-
TERRENCE P got a reaction from Jakac in Inverter Changeover TimeThis ups is always Online so "0" change over time. This ups is not affected by the main unit change over at the DB . This has been running perfectly for 2 weeks. My fridges are permanently powered and dont even skip a beat.
Works for me 100 %