March 26, 20206 yr Hey all ... I reached out to Dyness (China) for the settings required and battery cable configuration. I got a response the next day which was great. ---------- You need to make sure that the dip switch on the master battery is 0010. This is the default on battery from the factory. Make sure to update you Venus firmware to at least 2.42 For the can bus use : CAN-bus BMS (500 kbit/s) Make up a cable as per below: If all works well, then you should see "Dyness-L Battery" appear as a device on the Venus On the Venus set the following: Goto Settings -> System Setup -> Battery Monitor and choose "Dyness-L Battery on CAN-bus" Goto Settings -> DVCC -> Turn on DVCC Goto Settings -> DVCC -> Enable "Limit Charge Current" Goto Settings -> DVCC -> Set maximum charge current = 100A Goto Settings -> DVCC -> Turn OFF SVS Goto Settings -> DVCC -> Turn ON STS Goto Settings -> DVCC -> SCS should show as Disabled (External Control) On the Inverter set the following: Battery type = Lithium Charge Curve = Fixed Bulk Voltage: 53.5 Float Voltage: 51v Sustain Voltage: 49v Absorption Voltage: 52v Absorption Time: 1hr Cut off Voltage: 46v DC Input low shutdown: 44v DC Input low restart: 48v DC Input low pre-alarm: 48v Dynamic Cut Off Values: 46v (all options) Restart off-set: 1.2v Checking The Configuration Goto Dyness-L Battery -> Parameters. If the battery is fully charged then CCL should show as 0.0A and DCL as 120A (30A per battery). This means that the battery is talking to the Inverter Here is a list for other SOC's Hope this helps someone. Mine seems to be working well now.
March 27, 20206 yr The "turn on STS" bit is interesting. The idea of shared temperature sense is that one temperature sensor is used for all the equipment so that they can compensate for temperature. But when the BMS dictates the charge voltage, temperature compensation isn't done anyway... so STS does nothing. 🙂
March 27, 20206 yr Author I should just point out for the settings above I have the 9.6 kWh battery (4 x 25A)
March 27, 20206 yr Hi All Iam currently configuring a Victron Multi Plus II with two Dyness Powerbox F 9.6Kw batteries. Ive used the settings of OP's post but the CCGX only show 50ah capacity. Any help will be appreciated.
March 27, 20206 yr 2 hours ago, Armand said: the CCGX only show 50ah capacity That's what the BMS is sending in the CAN frame with ID 0x379. This is a fairly new extension to the CAN-bus protocol (November 2019), and it is a Victron initiative, ie we made it up, and the battery makers who want to integrate with us are expected to implement it (if they want to, it is optional, but really useful to have). Due to its newness, and the complete lack of support for the other items, I suspect they use 0x379 for something else and the 50 means something other than capacity. This is screen is for information purposes only and so far only a few battery makers support it (BYD Premium, Pylontech 24V battery). The value is not used for anything else and the fact that it is wrong does not affect anything. Just ignore it. Edited March 27, 20206 yr by plonkster
June 2, 20206 yr Hi Guys I can't get a Dyness B4850 battery to connect with my Victron Multiplus 2 GX. I have: Updated all Victron Firmware. Set the CAN-bus Profile - CAN-bus BMS (500 kbit/s) and used the Victron VE.Can to BMS CAN type B cable the right way around. Set DVCC on. Any ideas of where i'm going wrong?
June 2, 20206 yr 4 hours ago, Andrew P said: Any ideas of where i'm going wrong? What you can do is root the GX device, and then you can use an SSH client (PuTTy is commonly used on windows) to get a root shell on it. Then you can run candump to see the canbus communications. You'll probably type "candump can0", but here is an example from another type of GX device that has two CAN ports: root@beaglebone:~# candump can1 can1 1CEFFF24 [8] 66 99 20 01 18 03 00 00 can1 1CEFFF24 [8] 66 99 D5 ED 47 08 00 00 can1 1CEFFF24 [8] 66 99 8D ED 47 08 00 00 can1 305 [8] 00 00 00 00 00 00 00 00 can1 307 [8] 12 34 56 78 56 49 43 00 This one has a Victron VE.CanMPPT, which is why its sending these large 29-bit ids, but you should see something similar. If you see nothing (or if you only see the 0x305 and 0x307 frames), then there is no CAN-bus commications. 0x305 and 307 are keepalive messages sent by the GX device. If you see CAN-bus comms, and it is still not working, ask me again... I may know... 🙂
June 6, 20206 yr Problem solved. The Dyness B4850 batteries I had didn't have dip switches, my supplier swopped them out for units with dip switches and now all is good. New problem I just encountered with a multiplus 2 gx is the local wifi connection has vanished and not returned after rebooting the venus and restarting and whole system. Anyone else had issues with Venus GX units?
June 7, 20206 yr 22 hours ago, Andrew P said: Anyone else had issues with Venus GX units? Yeah, it's one of those recurring issues with Wi-Fi. I found that unless you have nice strong WiFi, it tends to drop out and not always return. Best is to rig up some ethernet to it, or invest in a Wi-Fi repeater.