Gerrie reacted to a post in a topic: Sunsynk 8KW Head Scratcher
-
Yellow Measure reacted to a post in a topic: Sunsynk 8KW Head Scratcher
-
@branderplank thanks for the info. Ill drop mine if this solves my problem, 200w is such a waste. I believe the Conlog inverters are rather sensitive. What meter do you have?
-
@YellowTapemeasure the non essential loads just don't work, the plugs/circuits are dead. And nothing trips. I might have found the problem, it seems that the prepaid meter(Conlog) is 'tripping' for like a minute, no errors on the meter though. I have turned up the 'Zero Export Power' from 20w to 200w and so far no issues. If this works ill incrementally drop this to the minimum(provided this works of course)...
-
@PowerUsermy CT coil is before the DB main breaker. When the power drops I’m reading 60v on my eskom feed, before DB, inverter etc...
-
Hi, I have a Sunsynk 8kw system with 4x Pylontech US2000 and 12 525w PV. All works fine except when I untick 'limit to load only'. My understanding is that this will allow excess power to feed back to the 'Non-essential/Eskom' side. The issue that I'm having is that in this mode I have power 'drop-offs' on 'Non-essential/Eskom' side. I.E. These circuits just have no power(they switch off) for periods. The issue is not load dependent as this happens with high and low loads but as soon as I tick the 'limit to load' the problem stops. Am I missing something? Please help. Thanks