Synapse V3.0+ & Hubble S1-00 Charge Issue
I ended up replacing my inverter and battery. Could not get the bulk charge issue resolved. All good now with the new setup.
-
Pylontech UP2500 to Must PV1800 BMS
Can anyone give advise on how to sonnect the pylontech UP2500 to Must pv1800 VPM inverter? I use the USB port on my inverter to connect to Raspberry Pi, to use Solar Assistant. What cable and ports do i use to connect the Pylontech to the MUST for BMS communication? What type COMS cable do i use?
-
Synapse 3.0V+ and Pylontech UP2500 (BMS Query)
Hi, I currently have a Synapse V3.0+, 24V inverter installed and want to replace my 2x S100 Hubble batteries, (only internal BMS). I can get my hands on a Pylontech UP2500 battery, but was wondering how the BMS interface would work with the inverter? What battery type setting do i select on the Synapse inverter? Do i set to USE and then the battery BMS controls te rest, charge voltage ranges, etc? Further to this, i also have a spare MUST pv1800 vpm inverter available and can replace the Synapse? Will this be a better solution to communicate with the Pylontech BMS? My current Synapse inverter is connected to a Raspberry Pi via CAN - USB for monitoring via SolarAssistant. This communication protocol is also not great as it requires continues rebooting of the system to re-establish the connection. Your thoughts or ideas would be appreciated.
-
Synapse V3.0+ & Hubble S1-00 Charge Issue
Yes, DC charge current. I have battery balancer with live viewing connected to the batteries at all times, so the voltages are correct eliminating bad terminations. Also confirmed with a multimeter. I can set the float and bulk to 28.8V, i doubt that this will change the charge current. My guess is the different charge cycle times need to be changed somehow... Agreed, i did not expect much, but was atleast hoping to achieve the advertised charged currents...
-
Synapse V3.0+ & Hubble S1-00 Charge Issue
Have you confirmed this with a clamp meter? Mine has a max grid charge current of 25Amps only, although it never reaches that. Only 7.2-7.3 Amps...
-
Synapse V3.0+ & Hubble S1-00 Charge Issue
@Scorp007, very interesting indeed. It can only be a charger issue then? My 2x S-100's charged at >40Amps and bulk voltage on previous inverter. Only now on the synapse that it is a issue. Had good solar available today and also did not manage to go over 7.2Amps, 28V.
-
Synapse V3.0+ & Hubble S1-00 Charge Issue
Thanks, i agree the PV is too small. This is what i had and plan to expand a bit in the future. It caters for my needs at the moment. Yes, seems the charging is not as expected on the inverter.
-
Synapse V3.0+ & Hubble S1-00 Charge Issue
0Amps at 28V.
-
Synapse V3.0+ & Hubble S1-00 Charge Issue
Installed System: Synapse V3.0+ (3000VA/2400W), 24V inverter with 2x Hubble S-100 batteries in series. Further to this a HA11 battery equalizer is installed. PV: 2x 180W panels. I use Solar Assistance to monitor the inverter, PV and batteries. Also confirmed the voltages with a multi-meter. Battery charge settings are: Charge: Utility and Solar simultaneously Source: Utility as priority Battery float charge voltage 28.0 V Battery absorption charge voltage 28.8 V Firmware: U1 09 56 U2 03 39 It seems the inverter charger never reaches the bulk charge voltage of 28.8V and never exceeds 7.2Amps. I have drained both batteries and connected them in parallell for a hour before connecting back to series and recharging. A/C charge set to 25Amp with max charge to 60Amp. I have tried to charge on solar & utility, utility only and solar only but cannot get the inverter to do a bulk charge. After the charge has been completed, the batteries are at 28V, 100% SOC. This is correct as per the hubble's recommended charge settings. I have searched for inverter firmware updates, but no luck. Any ideas what the problem could be, why i am not achieving a bulk charge?