I Have A Deye 5Kw Inverter and the CT coil is reading incorrectly, roughly 1.8 to 2kw over what is being used in the house, as a result "zero export to CT" causes the meter to report grid export. Due to the fact that it is not reading the true value of our home's consumption. E.g. home is using 2kw, CT coil reads 3.1kw, therefore the inverter supplements the "non-essential" loads with 3kw(1Kw more than what is actually being used) causing roughly 1kw to be fed back to the grid, even with zero export power set to 100W this is also shown on our City power Meter interface as a negative value confirming that power is being exported.
Even when the house is using roughly 400W, as shown by the Itron screen, the inverter still shows over 2KW as measured by the CT coil.
The installers have never seen this behavior before, and have tried changing the CT coil multiple times as well as performing 2 firmware updates.
The CT coil has even been moved to different locations, closer to the Meter to avoid any possible crosstalk between fields in the DB Board.
The CT coil used to read accurately, the suddenly just jumped up by 2KW and never went back to its normal correct/accurate readings.
Has anyone else experienced this or have any possible suggestions.