Unknown load on Non Essentials -Sunsynk 8kw
Yeah thanks I have a CAT 7 I plan to replace it with when I have time to do it properly
-
-
Unknown load on Non Essentials -Sunsynk 8kw
Just some feedback, Solved it , albeit it temporary for now - move the CT Clamp to the municipal feed box and ran 15meters of 0.5mm speaker wire to the inverter and now everything is running perfectly thanks for the inputs
-
Unknown load on Non Essentials -Sunsynk 8kw
Thanks guys , I guess my next step is to move the CT onto a CAT/lan cable and see if that improves things
-
Unknown load on Non Essentials -Sunsynk 8kw
Hello All Hoping to get some pointers on a problem I have with my Sunsync 8kw system. There is a constant load of 700-900watt on my non essential circuit. If export to CT is off it draws from the grid and if export to CT is on then it draws from the PV. On my non essentials is my geyser and poolpump , both are turned off at the DB when I took the attached screenshots. My installer confirmed the same consumption when testing for the problem but he only had 10mins to quickly look around but sadly he is away for a few weeks The CT coil is roughly 15-20m from the DB board and is connected using the standard cable type and not a CAT5/6 cable Anyone encountered this and can advise on a solution ?
HenryJ