Another installation, another CT Coil related issue
I've read just about every forum (including this thread), sunsynk manual, literature and video I could find relating to this topic and tried to follow every advice I could find, but I just can't seem to get a correct CT reading...
At least not based on my understanding - The CT Coil should be reading the amount of current coming from the grid.
System Mode - Zero Export only selected.
In my mind, this means that the reading should show more or less the same KW usage as what my eskom "smart" meter shows - But as you can see it is waaay off - In the test, I was drawing a combined load of 1.9 KW while my DC/panels are off and system timer is off which I believe is best practice while testing - 1kw was attributed to a non-essential pool, and the rest was essential load.
Should the CT reading show 1.9 kw as that is what is flowing through the CT?
The CT is installed in the box on the outside of my house's wall on the main feed line - The arrow is pointing towards the inverter (as documented) and the white wire is connected to port 3 and black to port 4 - Using a Sunsynk 5.5kW inverter, so believe this is correct - Also when switching either around, the reading becomes negative so pretty sure everything is the right way around.
I did extend the cable - The total length for the testing cable is just about 10m +- a couple of centimeters.
I used CAT6e cable and only one pair - I also matched the twist direction (i think) as suggested.
It is currently lying along the floor to eliminate any other interference.
Attached is all other settings I though might be relevant.
Is the CT Coil model and specs correct?
Is there something wrong in my understanding?
Any settings that should change?
How do I as a non-electrician test that the CT coil by itself is working correctly?
Last question to check my understanding - When you change the system mode to "Limit to load", it then uses an internal CT coil and does not need the external one, right?