Dear @SolarConvert, @Jay-Dee et. al, I were able to communicate my Narada 48NPFC100 with Deye 8KW hybrid inverter. But there is slight problem, After getting the BMS data on inverter screen, the SOC reading drops to 1 % and then revert back to actual value. Firstly I thought, could be because of my cable connections, so I changed the cable but the problem persists. Then I assumed that the inverter might be mis-interpreting the data because my battery was 100 % charge and its the problem of rounding off the decimal point i.e. 100 -> 1.00 so I discharged my battery to any other value but still the SOC BMS readings were going back and forth.
At this point, I assumed, the problem is my battery BMS or my inverter. so I asked another guy to test these combination ( given below) and he had the same exact problem. Can you please guide me which combinations should I try more since you have grabbed the BMS data by logger and analysed it.
inverter pin 1 (white orange)--> battery side pin 6 (solid green)
inverter pin 2 (solid orange)--> battery side pin 7 (white brown)
BMS mode 16
Port: CAN
thanks in advance,