DarkGhost reacted to vanguardviper in Deye Hybrid Inverter takes a few seconds to switch to off-grid when grid goes offSwitching from grid to battery is a signal from control to Relay ... If we assume the relay is working fine, then we check load.
you said Load is 500 to 1 Kw .. that shouldn't make that problem for a 10KW inverter ..
so I advise:
- check grid status (Voltage, Frequency) if the grid voltage is lower than normal that could cause that delay (solution is a good regulator)
- check Cables, if cables diameter is not well calculated or the length between inverter and load is big, that will cause drop voltage which get us back to first case.
- check inverter settings, especially the response time (usually there are two options, one for appliance (20ms) and one for sensitive devices like PCs (lower than 10ms)
- check battery condition, and concentrate on terminal connections, also check connections on circuit breakers if there is any.
- If your system is NOT a common Neutral (combined grid Neutral with inverter output Neutral) that could cause such a problem (thou I don't recommend that kind of install)
I advise you to use a small UPS for sensitive devices (routers, PCs .. etc.)
Actually, I've done this with my own system because I have the same problem you have, SPECIFICLY when gaming on my PC
hope that help ...
-
DarkGhost reacted to madness_za in Deye Hybrid Inverter takes a few seconds to switch to off-grid when grid goes offDo you know what the load is when this happens?
-
DarkGhost reacted to JustinSchoeman in How far should I regularly discharge lithium battery on solar pv system for optimum long term cost minimization?Possibly one of the most comprehensive tests was done by Sandia National Labs:
https://iopscience.iop.org/article/10.1149/1945-7111/abae37/pdf
The bottom chart shows the total kWh discharged from the battery from new until it degraded to 80% of its initial capacity.
There is roughly 20% improvement between 100% and 20% DoD. The difference between 60% and 20% is negligible. Would have been nice to have more data points to find where the knee point is, but it is certainly not much to be gained going much below 60% DoD.
What is striking though, is how much difference other factors (temperature and C rating) make. If you really want the most from the cells, then:
1) keep them cool, and
2) stick at or below 1C discharge.
-
DarkGhost reacted to HendrikBigChief in Deye Hybrid Inverter's "Use Batt %" setting and available sub-menu optionsIn general it is not a good idea to only charge to 80%, especially if using LFP lithium. The battery needs to go to 100% to reset the SOC algorithm and (in some instances) balance all the cells properly.