You should do calculations on your side otherwise you going to damage your inverter. if you go according to the manual that yo get with the inverter. A 50Kw inverter is actually 3 x 16,66Kw single phase inverters. Your supply from your utility to inverter is a 100A 3p breaker and your return is a 80A 3p breaker. I have done 5 x 50Kw systems and don't have any issues. if you install a 250A breaker as they say in the Manual you are going to damage your inverter, I find on a lot of re installs that the guys doesn't have any knowledge of how to do the correct calculations, even for a 5Kw or a 8Kw. if your a real installation electrician you will have the knowledge to do the calculations and not follow the manual that is wrong.