Everything posted by zs1ssm
-
Growatt Wifi Datalogger Problems
After I do a full reset I can connect to the datalogger`s wifi but I can not connect to the GUI of the datalogger---error refused connection---Next time I am using a hammer for complete reset !!!!
-
Growatt Wifi Datalogger Problems
My dongle is connecting to my router but not to the server--tried resetting, deleting dongles, deleted the app , reinstalled the app,,even created a new account, but data logger only connects to the router and not server !!!! Please some help here
-
Lights Dimming
Had a check on the cable size from the inverters to the db box and the size is the same as the "eskom" incoming lines--So I think that the inverters initial power boost (is that what you call it) is to low
-
Lights Dimming
Thanks all---Just to add --Each battery is bridged to the inverters-- One 5kw inverter has 10mm from one battery and the second one is the same--The bridge is between the 2 batteries --so 10kw is shared by 2x10mm cables--I could be wrong--But system is running 100%--Only problem is that the Growatt dongles can not be combined to give the combined reading --Some one at Growatt that can assist ????
-
Lights Dimming
Hi--it is 2x5kwh batteries supplied by LithiumSA --Batteries are in parallel with 10mm wires to inverters
-
Lights Dimming
Observed that my lights dims for a fraction of a second when one of my fridges starts up--Even with the VICTRON 8KW (Loan unit) I saw that--Now I am running 2x5kw Growatt inverters ---Is it that the capacitors in these are to small ?? If it is the issue can I install an external capacitor between the inverter output and db board ??? Cheers Mark
-
2 x Growatt SPF5000ES shine/server app
Sorry I have tried that it does not work
-
2 x Growatt SPF5000ES shine/server app
I have 2 x 5kw growatts in parallel and both has it`s own dongle--On the shine app and the server I can only view one inverter`s output at a time --I can switch between the two inverters but that is not what I want--I need the combined output and PV input---On the (All Devices) page I can get the combined power that was generated---Any help please----Sorry I do not have a raspberry pi
-
Isp tool to upgrade a Growatt inverter firmware
Please send the files to me as well
-
Vito 8.2kw inverters
Anyone has experience of the Vito inverter range --Looks like a decent inverter but before I buy I would like a review on them---Looking at the 8.2 KW to replace my Growatt 5kw es inverter
-
Inverter Neutral Earth bonding
Sorry to say --I did a test while system is drawing power from the grid and the voltage between N and E is 0v but if the inverter runs off batteries or just solar then 80v are present--so that tells me the inverter is not bonding the NE--Growatt SP5000ES 5KW
-
Earth Leakage Trip
So , installing some diodes in the incoming pv lines will solve the problem ????
-
Earth Leakage Trip
Ok--Now I have removed all 8 solar panels and checked all connections---Dry dry dry!! :(---TEsted the Growatt SPF5000ES solar input and got 196 volt ac !!!---Is is supposrd to do that ???? Pos and Neg =200v pos or negative and earth =196v--what can I do to rectify this ? ---Cheers
-
Inverter Neutral Earth bonding
Looks like I have started a very confusing post The smart meters / pre-paid meters dont they have reverse protection build in ??
-
Earth Leakage Trip
Hi --it is a Growatt spf5000es---If both + and - are disconnected then el does not trip but if I connect anyone then the el trips--Eskom and inverter comes in at the change over switch and from there to the el---(eskom on it`s own input and inverter on it`s own)
-
Earth Leakage Trip
Just a question please ??? If I feed my solar panels to the inverter and it starts to rain ,my earth leakage trips out--even with all switches off at the db board--on eskom power everything is ok --I have checked all connections and no shorts are visible and all connections are dry--My roof is Aluzinc and roof is earthed to a separate spike into the ground--It is almost like the phase going mad when it rains--Even if I disconnect only neg or pos then same symptoms. I even replaced my el. The installer "left the country"
-
Inverter Neutral Earth bonding
Can anyone confirm if the Growatt SPF5000ES does the E/N bond or not ???
-
Inverter Neutral Earth bonding
Can anyone confirm if the Growatt SPF5000ES does the E/N bond or not ???
-
Inverter Neutral Earth bonding
Some say yes some say no ???? My setup are the following as per drawing. Now if I bond the neutral and the earth from the inverter and work hat to be done on the electrical box outside (eskom) then the earth back to the box will have a earth that can carry current due to the bonding---My inverter do not do the bonding as I tested the system---On eskom power the e/n there is no voltage but on inverter there is 84volt between e/n. Anyone please explain if I can bond earth/neutral at the inverter out and also the feedback from the bond to the electrical box outside
-
Growatt SPF5000ES tripping earth
All appliances has been isolated at the DB box (switched off) and as soon as the solar is fed into the inverter then the EL at the db trips--Almost as if the phase between live and neutral goes out because there is no earth connected
-
Growatt SPF5000ES tripping earth
Can not believe no one has a answer for me SO the question is ----To BOND or NOT TO BOND
-
Growatt SPF5000ES tripping earth
That is exactly how it is connected----Even with the feed from eskom disconnected it sometimes trips the EL---I did reset now and is running fine---Until the next trip ----Do I need to bond the Neutral and earth at the inverter ??
-
Growatt SPF5000ES tripping earth
Sorry this only happens when the inverter is supplying the house without Eskom
-
Growatt SPF5000ES tripping earth
Some help please---My Growatt SPF5000ES randomly trips the earth leakage in my db box even with all breakers switched off----Reset everything and then works for about 2 to three days then trips again---Some times if I disconnect the solar input negative and positive then the system would run for weeks before tripping the EL---My installer said that I need to bond the Earth and Neutral at the inverter and my problem will go away---???????????
-
Growatt SPF5000ES
Something weird happened---This morning when I woke up I noticed that my inverter is in bypass mode and that the batteries are disconnected (batteries full)--I did not change any settings and it ran fine for the past 3 months----Did a reset and now working as normal again--Anyone have a clue as what could cause this? Cheers