Hi All

I think this is a relatively easy question and I'm sure it has been asked before I just can't seem to figure it our for myself. 

I have a Deye 8kW hybrid inverter. Under the System Work Mode (SWM) menu I am only able to set my battery SOC to 35%, no lower. I want to set this value down to 25% but there must be another setting somewhere that is stopping me from doing this. 

The inverter is set give a low battery warning at 35%,shut down at 20% and restart at 50%

Could anybody please tell me what else I need to set to be able to bring my SWM battery SOC down to 25%.

Thanks in advance! 

Somewhere on the battery screens you have to set alarm, shutdown and restart SOCs. One of those is limiting the minimum you can set on the system work mode screen. Think BattSet3.

Edited by Scubadude

1 hour ago, Freakazoid said:

The inverter is set give a low battery warning at 35%,shut down at 20% and restart at 50%

That's it yes! Mine is warning at 15, shutdown at 10 and restart at 20. You can make yours warning at 20, shutdown at 15 and restart at 25 if you want tot go down to 25%

  • 10 months later...

Awesome - I have the same problem… 8kw hybrid with Freedom Won battery … won’t let the battery supply below 30% but FW battery specifies this to be 20%… so I want to change this 30% parameter to 20%… or I am wasting this warrantied capacity on low solar days 

 

was there a resolution to this ?