June 13, 20224 yr Hi Guys, Has anyone gotten it right to use 2 x Leoch LEeLI-48100T with a Sunsnyk 8kw system so that SOC and battery info is received by the inverter. I have one battery working correctly via CAN However, I have followed the Averge guide (Set battery 1 and 2 address dipswitch, and connect via RS486 B and C to battery 1 and 2) The Inverter still only reports LIBMS01 constantly and doesnt seem to see the secondary battery. Any trick on how to do this?
January 9, 20233 yr Hi Chris, did you ever get this resolved? Do you have some pictures or a wiring diagram on how you connected the Cables? I have 3 of these Batteries and im not sure how to wire the RS485 cables between the master and pack1 and pack2,
January 10, 20233 yr 18 hours ago, Chubbs said: I have 3 of these Batteries and im not sure how to wire the RS485 cables between the master and pack1 and pack2, I have 4 of them. Use the delivered RS485 jumpers between packs and a RS485/USB adapter to a laptop. Set the dip switches accordingly. Works fine with PmodbusToos. Can monitor each BMS individually. The RS485 protocol works like a data bus. There is no master or slave. Each user is addressed with its binary address. I do not have connection of BMS to the inverters. Edited January 10, 20233 yr by Beat