January 16, 20233 yr I have a synsynk 8kw installed last week. No Solar panels. For backup for load shedding (panels will be added at some point in future. So, the situations is as follows: 1. The CT value is a negative. 2. After investigation i found that the ct coil is installed inside the inverter just infornt of the grid connector I am meeting with the installer tomorrow to discuss. This is obviously not correct and i need him to rectify. Can you please point me to the literature where it specifically states that these 2 items are incorrect. (Note that i have no clue about electrical work) The last point is that the db is about 15m in cable lenght away from inverter. Is this length ok for the CT to be installed in the DB?
January 16, 20233 yr 17 minutes ago, Frani said: I have a synsynk 8kw installed last week. No Solar panels. For backup for load shedding (panels will be added at some point in future. So, the situations is as follows: 1. The CT value is a negative. 2. After investigation i found that the ct coil is installed inside the inverter just infornt of the grid connector I am meeting with the installer tomorrow to discuss. This is obviously not correct and i need him to rectify. Can you please point me to the literature where it specifically states that these 2 items are incorrect. (Note that i have no clue about electrical work) The last point is that the db is about 15m in cable lenght away from inverter. Is this length ok for the CT to be installed in the DB? Negative reading from CT means it is installed incorrectly. The arrow must point to the inverter. It must be installed on the L wire between grid and DB. Search this site for how to extend the wire from CT.