MYBRIDH Posted January 24, 2023 Share Posted January 24, 2023 (edited) Good day all. Hope you are doing well. Question relates to the PSW-H-5KW-230/48V. I bought it a good while ago, not yet installed. At the time, I was under the impression that it had 2 MPPTs which it turns out is not the case. I back then bough half a set of panels for the one MPPT, not having a second MPPT as I thought, I have been hunting in vain and not able to find a matching set for the other PV input. So, I need a complete set of panels. My question is , as compared to the specs, how much PV can I actually connect to this inverter? Manual states: Max PV voltage = 450V MPT range = 120 - 430V Max usable PV Current = 22Adc Max usable PV Power = 4800W Max PV array power = 6000W To elaborate on the question: If I had two strings of panels , with 22A total Imp capability but enough panels that the voltage was at the upper end of the MPPT range at 343V, would equate to power capability of 7.5kW. Yet from both a current and voltage point of view it is within range. This though exceeds the Max PV array power = 6000W...........Should this 6000W limit be taken literally or would it generally be ok as long as the current and voltage are within stated ranges? Looking at it from another point of view, if the current capability of the PV array was such that it could provide more than the 22A but still within MPPT voltage range, would the inverter just limit its consumption or would I turn the inverter into a smoke machine? If this has been covered before, please do point me in the direction of that discussion. Thanks for taking the time to read this, answers to these questions would really help my efforts to not screw up when buying panels again. Regards Kassie Edited January 24, 2023 by MYBRIDH Quote Link to comment Share on other sites More sharing options...
MYBRIDH Posted February 6, 2023 Author Share Posted February 6, 2023 Bump.....nudge.....nudge...... Quote Link to comment Share on other sites More sharing options...
Coulomb Posted February 6, 2023 Share Posted February 6, 2023 Personally, I would not exceed the 6 kW. The issue will be overshoots. With more panel power than it's designed for, small changes in PWM ratio will result in large changes in charge current. If it was a really solid name brand, perhaps, but Phocos doesn't strike me as being one of those. I could be wrong. Quote Link to comment Share on other sites More sharing options...
MYBRIDH Posted February 7, 2023 Author Share Posted February 7, 2023 On 2023/02/06 at 6:42 AM, Coulomb said: Personally, I would not exceed the 6 kW. The issue will be overshoots. With more panel power than it's designed for, small changes in PWM ratio will result in large changes in charge current. If it was a really solid name brand, perhaps, but Phocos doesn't strike me as being one of those. I could be wrong. Much appreciate the feedback thank you Coulomb. I will try and err on the cautious side. Quote Link to comment Share on other sites More sharing options...
Recommended Posts
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.