February 24, 20233 yr Hey all, In regards to a 8KW Deye Inverter, what would happen during non-loading shedding when excess load is pulled. e.g. total 10KW Geyser 3kw Aircon 2kw Kettle 1kw hairdryer 2kw other 3kw Would it bypass to make use of Eskom power or would something trip or would the house blow up Thanks!
February 24, 20233 yr 8kw can passthrough to UPS / Essentials up to 11kw while eskom is around. If there is LS then it will trip at 8kw. That trip is also battery dependent - if you only have 1 0.5C battery then you are limited to that as well
February 24, 20233 yr Author 17 minutes ago, mzezman said: 8kw can passthrough to UPS / Essentials up to 11kw while eskom is around. If there is LS then it will trip at 8kw. That trip is also battery dependent - if you only have 1 0.5C battery then you are limited to that as well Awesome, thank you very much for that!!