February 24, 20233 yr We installed a Top Solar 3KVA Inverter with 2 Ritar 12V 100AH Gel batteries to keep 16 9W LED lights and 4 14W spot lights on during loadschedding. The lights are connected to a day night switch. The spotlights only comes on when triggered. Average load 160W at 5A. The batteries only last for and hour. Voltage drops and inverter shows low battery and switches of. Is this normal? Or do we need more batteries? Attached the Inverter specs and photo of brand new batteries. Any thoughts/ help welcome.
February 25, 20233 yr 5 hours ago, Pjs100 said: We installed a Top Solar 3KVA Inverter with 2 Ritar 12V 100AH Gel batteries to keep 16 9W LED lights and 4 14W spot lights on during loadschedding. The lights are connected to a day night switch. The spotlights only comes on when triggered. Average load 160W at 5A. The batteries only last for and hour. Voltage drops and inverter shows low battery and switches of. Is this normal? Or do we need more batteries? Attached the Inverter specs and photo of brand new batteries. Any thoughts/ help welcome. Do you have a multi meter to double check the voltage readings? Are the batteries new or used?
February 25, 20233 yr Author 2 hours ago, Stefan Cornelissen said: Do you have a multi meter to double check the voltage readings? Are the batteries new or used? Yes we tested the voltage and all seems fine. Also checked the batteries with a load tester. The batteries are brand new and also tested when we picked it up at the supplier.
February 25, 20233 yr 58 minutes ago, Pjs100 said: Yes we tested the voltage and all seems fine. Also checked the batteries with a load tester. The batteries are brand new and also tested when we picked it up at the supplier. Did you test with only a short term load tester? These testers can give a all good reading but can still lack capacity. Also one MUST ensure the batteries are fully charged which might be the problem. Post your bulk and float settings on the inverter. Also post the settings for back to grid and back to battery as well as cut out. Those batteries should give at least 8hrs run time up to the level of SOC of 50%.
February 25, 20233 yr Author 2 hours ago, Scorp007 said: Did you test with only a short term load tester? These testers can give a all good reading but can still lack capacity. Also one MUST ensure the batteries are fully charged which might be the problem. Post your bulk and float settings on the inverter. Also post the settings for back to grid and back to battery as well as cut out. Those batteries should give at least 8hrs run time up to the level of SOC of 50%. Bulk 29.3 Float 29.1 The Inverter is set to USB. No pannels connected. Cut out at 20V
February 25, 20233 yr 2 hours ago, Pjs100 said: Bulk 29.3 Float 29.1 The Inverter is set to USB. No pannels connected. Cut out at 20V Some settings need to be revised otherwise you going to kill them batteries in a short time. Bulk 28.8 or closest on the down side. Float 27.5V Cutout 24V How old are those batteries?
February 25, 20233 yr Author 20 minutes ago, Scorp007 said: Some settings need to be revised otherwise you going to kill them batteries in a short time. Bulk 28.8 or closest on the down side. Float 27.5V Cutout 24V How old are those batteries? They are new.
February 25, 20233 yr 2 hours ago, Pjs100 said: They are new. Try and replace. With your high settings if they had enough time to fully charge you should easy get the 8hrs I mentioned.