Posted March 19, 20232 yr Good Afternoon Gentlemen I have the following issues I have a 8 KW Sun Synk inverter and 2 Hubble AM 5 batteries. I don’t have solar as yet. All my essentials is on one phase in the garage and all connected to one phase the blue phase. When we get load shedded the inverter kicks in immediately with no issue. Once load shedding is over and GRID kicks in. It stays on INVERTER MODE for at least a hour before it switches back to GRID - Not sure why. We also experienced a bit of flickering during load shedding when inverter is ON only only lights. Please assist me I am not sure if System settings are correct.
April 10, 20232 yr Author By Inverter mode I meant the inverter kicks in. Is it possible I that I can please call you
April 10, 20232 yr On 2023/03/19 at 11:30 AM, Reeza said: Once load shedding is over and GRID kicks in. It stays on INVERTER MODE for at least a hour before it switches back to GRID - Not sure why. Check in your Settings, Grid Setup, Grid Type, then look for Grid Reconnect Time. This is normally set to 60 seconds, yours sounds like it's set way higher. If it's not 60s adjust it down 60s, and see what happens during the next load-shedding, or test by switching your mains MCB off and on again. Oh, and welcome to the forum, and Power independence, especially when you get panels too. 👍 Edited April 10, 20232 yr by TimCam