Max Charge/Discharge
Hi,
I have two Deye 5kw inverters hooked up in parallel. Both are connected to a single 10kwh Lithium battery. Battery details can be found here (I have the LFP200-51.2). The battery manual says the max charge and discharge current is 100A.
My question is, since I have two inverters should I set the Max A Charge and Max A Discharge on each inverter to 100 A or should it be 50 A per inverter to make up the 100 A?
Thanks.
Regards.
Thanks.
And based on the battery manual shared above, what should the following three parameters be set to ( in Volts)?
1) Battery float charge?
2) Battery absorption charge?
3) Battery equalization charge?
Edited by QB87
I don't have any knowledge or experience on these batteries. If this was my battery, looking at the Spec sheet, I would set the following parameters:
1) Battery float charge = 52.5V
2) Battery absorption charge = 53.0V
3) Battery equalization charge = Off (disabled)
With these settings you should still be able to achieve 100% SOC without cooking the battery at max. voltage.
Edited by Don